I am looking at purchasing a '92 Bounder and have a question. Should both roof top AC's be able to be run at the same time. Iff not is this something all Class A's have in common or just Bounders'.
I am looking at purchasing a '92 Bounder and have a question. Should both roof top AC's be able to be run at the same time. Iff not is this something all Class A's have in common or just Bounders'.
YOU SHOULD BE ABLE TO RUN ABOTH THE AC'S AT THE SAME TIME IF YOU ARE HOOKED TO A 50AMP POWER SOURCE. I DON'T KNOW WHAT TYPE OR SIZE YOUR GENERATOR IS. YOU MIGHT NOT BE ABLE TO RUN BOTH AC ON THE GENERATOR AS IT CAN'T HANDLE THE AMP DRAW. HAROLD
I am looking at purchasing a '92 Bounder and have a question. Should both roof top AC's be able to be run at the same time. Iff not is this something all Class A's have in common or just Bounders'.
Coaches with 50 amp service are set up to run both AC units. Many older coaches with 30 amp service are set up with 2 AC units but only one can be run at a time from shore power. Some of these 30 amp units are capable of running both AC units from the generator if adequately sized.